What is the minimum number of 120 volt, 20 amp branch circuits required for the lighting of a 6,000 square foot restaurant?

Get ready for the Limited Licensed Electrician exam with our interactive quiz. Use flashcards and multiple choice questions, complete with hints and explanations for thorough preparation. Ace your test!

In determining the minimum number of 120-volt, 20-amp branch circuits required for the lighting of a 6,000 square foot restaurant, it’s essential to refer to the National Electrical Code (NEC) standards that guide branch circuit calculations for general lighting loads.

Typically, each 120-volt, 20-amp circuit can safely power up to a certain wattage (commonly 1,920 watts), and the calculations for commercial lighting loads may use a standard of 3 watts per square foot for general lighting needs. For a restaurant that is 6,000 square feet, the total lighting load would be calculated as:

6,000 square feet x 3 watts per square foot = 18,000 watts.

To determine how many circuits are needed, divide the total load by the capacity of one circuit:

18,000 watts ÷ 1,920 watts per circuit = 9.375 circuits.

Since you can't have a fraction of a circuit, this number rounds up to 10 circuits. Depending on local codes or specific restaurant design requirements, it may typically fall within a practical range for lighting circuits. However, this specific question is gauging the minimum number required, and based on standard practices, having